So is GG question about 208 vs 240? Aren't they the same thing essentially?Yes it will be supplied by 120/208. I'm guessing that the panel is rated for 120/240 as you've stated.
So is GG question about 208 vs 240? Aren't they the same thing essentially?Yes it will be supplied by 120/208. I'm guessing that the panel is rated for 120/240 as you've stated.
For line to neutral loads, yes, but not for line to line loads.So is GG question about 208 vs 240? Aren't they the same thing essentially?
Heating equipment with a rated wattage of 4000 watts at 240, will only have an output of 3000 watts at 208. Some motors intended for 240 volts don't like a 208 volt supply.So is GG question about 208 vs 240? Aren't they the same thing essentially?
Thanks...sometimes this electrical stuff is complicated.For line to neutral loads, yes, but not for line to line loads.