winnie said:
Bump. Is my thinking here reasonable, or am I still out to lunch

?
-Jon
I'll jump in here....Although your scenario is not the way that it's done where I live, On Undergrounds, the POCO runs high voltage underground (in the customer's trench) to a POCO provided transformer located near the home. From there the POCO will run to the customer's meter can (through customer's trench and riser).
I haven't had any experience with your problem, so, any opinion that I give will be fwiw.
When I first read your post I thought..no way. It understood it to say that you wanted to run 2 ungrounded (hot) conductors to the 600/240 transformer and not run a grounded (or grounding) conductor. Then use a earth ground to provide grounding and bonding for the transformer case and center (neutral) tap of the wye connected transformer. This earth ground also providing the grounded (neutral) for the house.
After reading the posts, I think that what you mean is to run 1 ungrounded (hot) and (1) grounded conductor from the first transformer to the second transformer disconnect. At that point you will install a earth ground and bond this grounded conductor to the transformer case, grounded conductor (supplying the house) and center tap of the wye connected transformer. Am I doing OK so far?
If that is the case, then IMO the disconnect (service rated) at the second transformer will be the service Main. From this main disconnect the grounded (neutral) and grounding conductors need to be seperate, requiring a 4 wire feed from the transformer to the house. A Grounding electrode will also need to be installed at the house and bonded to the grounding conductor from the transformer and the breaker panel in the house.
(IMHO) this set-up is OK.
As I said, I don't have much experience with service transformers as the POCO does all of that.
Just thinking out loud.
Any comments? Am I off base?
steve