This is from the December 10, 2012 minutes as listed on NC DOI website. Note addition of item 3.
Item D-24 Request by Robert Privott, NC Home Builders Association, to amend the 2011 NC Electrical Code, Section 404.2 (C). The proposed amendment is as follows:
Section 404.2 (C) Switches Controlling Lighting Loads
(C) Switches Controlling Lighting Loads. For switches controlling lighting loads supplied by a grounded general purpose branch circuit, the grounded circuit conductor for the controlled lighting circuit shall be provided at the switch location.
Exception: the grounded circuit conductor shall be permitted to be omitted from the switch enclosure where either of the following conditions in (1), or (2) or (3) apply:
1. Conductors for switches controlling lighting loads enter the box to a raceway. The raceway shall have sufficient cross sectional area to accommodate the extension of the grounded circuit conductor of the lighting circuit to the switch location whether or not the conductors in the raceway are required to be increased in size to comply with 310.15(B)(2)(a).
2. Cable assemblies for switches controlling lighting loads enter the box through framing cavity that is open at the top of bottom on the same floor level, or through a wall, floor, or ceiling that is unfinished on one side.
3. Residential one- and two-family dwellings.
Motion/Second/Adopted as modified ? This motion was passed unanimously