W wellin New member Apr 29, 2009 #1 We are installing a 208V 3Phase sub-panel fed from and existing 208V 3Phase panel. There will be only 3Phase loads on the sub-panel. Are we required by the NEC to run a neutral to the sup-panel?
We are installing a 208V 3Phase sub-panel fed from and existing 208V 3Phase panel. There will be only 3Phase loads on the sub-panel. Are we required by the NEC to run a neutral to the sup-panel?
A/A Fuel GTX Senior Member Location WI & AZ Occupation Electrician Apr 29, 2009 #2 Nope......Not Necessary
raider1 Senior Member Staff member Location Logan, Utah Apr 29, 2009 #3 Welcome to the forum. There is no NEC requirement that you must bring a neutral conductor to a remote panel board if there is no line to neutral loads at the panelboard. The NEC only requires that a grounded (neutral) conductor be brought to a service. Chris
Welcome to the forum. There is no NEC requirement that you must bring a neutral conductor to a remote panel board if there is no line to neutral loads at the panelboard. The NEC only requires that a grounded (neutral) conductor be brought to a service. Chris
A/A Fuel GTX Senior Member Location WI & AZ Occupation Electrician Apr 29, 2009 #4 The "Welcome to the Forum" is what got you Chris
raider1 Senior Member Staff member Location Logan, Utah Apr 29, 2009 #5 A/A Fuel GTX said: The "Welcome to the Forum" is what got you Chris Click to expand... Yep, I'm just too nice of a guy. Chris