They want to oversize the neutral on the output
Neutral output wires: rate for 173% of output phase current if feeding
all Switch Mode Power Supply loads without power factor
correction
Single phase non-linear loads producing third harmonic.They want to oversize the neutral on the output
Neutral output wires: rate for 173% of output phase current if feeding
all Switch Mode Power Supply loads without power factor
correction
I have forgotten how to do the math on this one. But what I recall is that the maximum current that can flow in the neutral of a balanced system that has harmonics present is equal to the current in the phase conductors times the square root of three (approximately 1.732). The rest of this response will have to be supplied by others.I should have been clearer, the input is 208/120 with a 1.73% over sized neutral or on the load?
I guess that is where the 173% comes from. :thumbsup:current in the phase conductors times the square root of three (approximately 1.732).
I think there is no one size fits all solution. The shape of the waveform determines harmonic content.I have forgotten how to do the math on this one. But what I recall is that the maximum current that can flow in the neutral of a balanced system that has harmonics present is equal to the current in the phase conductors times the square root of three (approximately 1.732). The rest of this response will have to be supplied by others.
Not exactly what it states.In this white paper from APC they state that the theoretical highest harmonic current to be 1.7X the phase current.
Quite a few caveats in there.The theoretical maximum neutral current will be 1.7 of the rated phase current value, if
all circuits are loaded to max rating, no loads are above 675 W, and all loads are generating
third harmonic at the compliance limit.
They want to oversize the neutral on the output
Neutral output wires: rate for 173% of output phase current if feeding
all Switch Mode Power Supply loads without power factor
correction
It has been a long time since I've seen neutral currents >100% of the phase current. Years ago, this was a problem, but not recently in loads I've seen, especially at the point of service entry (PCC).
Not exactly what it states.
Quite a few caveats in there.