Commonly known as a 200% neutral. Technically the ungrounded conductors have been upsized so the EGC may be too small.
I thought in most cases the neutral was the grounded conductor.
You bring up a point though, do I have to increase the size of the EG when the neutral is oversized but not the Phase conductors? I wouldn’t, but I’ve been wrong at least once....in the last 10 minutes.
We don't know that. The OCPD could be a 100 amp breaker. That properly corresponds with a #2 ungrounded conductor and a #8 EGC.Technically the ungrounded conductors have been upsized so the EGC may be too small.
We don't know that. The OCPD could be a 100 amp breaker. That properly corresponds with a #2 ungrounded conductor and a #8 EGC.
We don't know that. The OCPD could be a 100 amp breaker. That properly corresponds with a #2 ungrounded conductor and a #8 EGC.
I agree, EGC likely needs proportional increase in size in this case unless we can come up with a detail that says #3 isn't a 100 amp conductor for this application.Could be or maybe not. #3 THHN is a 100 amp conductor so #2 would be an increase in size from #3.
Scratch this....now I see where you came up with oversized phase conductors.:dunce:I thought in most cases the neutral was the grounded conductor.
You bring up a point though, do I have to increase the size of the EG when the neutral is oversized but not the Phase conductors? I wouldn’t, but I’ve been wrong at least once....in the last 10 minutes.