It was for odd order harmonics during the paranoria years and it has gotten permanately stuck in some designers minds.

Roger
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Commonly known as a 200% neutral. Technically the ungrounded conductors have been upsized so the EGC may be too small.
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Commonly known as a 200% neutral. Technically the ungrounded conductors have been upsized so the EGC may be too small.

I thought in most cases the neutral was the grounded conductor.

You bring up a point though, do I have to increase the size of the EG when the neutral is oversized but not the Phase conductors? I wouldn’t, but I’ve been wrong at least once....in the last 10 minutes.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I thought in most cases the neutral was the grounded conductor.

You bring up a point though, do I have to increase the size of the EG when the neutral is oversized but not the Phase conductors? I wouldn’t, but I’ve been wrong at least once....in the last 10 minutes.

250.122(B) references increasing the EGC only when the ungrounded conductors are increased in size.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Technically the ungrounded conductors have been upsized so the EGC may be too small.
We don't know that. The OCPD could be a 100 amp breaker. That properly corresponds with a #2 ungrounded conductor and a #8 EGC.

 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
We don't know that. The OCPD could be a 100 amp breaker. That properly corresponds with a #2 ungrounded conductor and a #8 EGC.


Could be or maybe not. #3 THHN is a 100 amp conductor so #2 would be an increase in size from #3.
 

kwired

Electron manager
Location
NE Nebraska
Could be or maybe not. #3 THHN is a 100 amp conductor so #2 would be an increase in size from #3.
I agree, EGC likely needs proportional increase in size in this case unless we can come up with a detail that says #3 isn't a 100 amp conductor for this application.
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
I thought in most cases the neutral was the grounded conductor.

You bring up a point though, do I have to increase the size of the EG when the neutral is oversized but not the Phase conductors? I wouldn’t, but I’ve been wrong at least once....in the last 10 minutes.
Scratch this....now I see where you came up with oversized phase conductors.:dunce:
 