kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
I understand and yes it seems many tubs do state minimum conductor size - even larger then what seems necessary on ungrounded and EGC in some instances. Seen many hot tubs that require 6 AWG on all conductors yet don't really give you space to install them very easilyK wired, I agree with you however 110.3(B) will most likely be the deciding factor here. Knowing the manufacturer and model of hot tub would help significantly in answering the original posters question. As I wrote before there is a decent chance that this hot tub does not even require a neutral. If it does number 8 would be more than sufficient the neutral would never see more than 40 amps, it's unlikely that , even if needed, it would see 15 amps. Article 680 installs are nothing to Monkey around with however I do not see a problem here with running a number eight neutral to the hot tub
Also agree 680 installs aren't something to monkey around with but still don't see how running a 14 AWG neutral makes any significant increased hazard to the user if it isn't loaded to more then it's ampacity. GFCI and bonding are the main things that make differences here.