??Originally posted by bphgravity:
Assuming you question does not pertain to a 4-wire, wye-connected, 3-phase system,
All phase conductors are counted. As to whether to count the neutral, see 310.15(B)(4). This still leaves open the question of how much harmonic current can the system contain, before it becomes a ?major portion of the load.? The code does not give a value, so it is left up to the designer and the approval authority.Originally posted by izak:What is considered a 'current carrying conductor' and what is not and why?
What should we do when bidding a multiple feeder job? If I bid it with full sized neutrals I will not get the work. How can I pass up the savings inherent in sizing the neutral only for the maximum imbalance? Why would I size the neutral for current it will never carry?
--
Tom HorneYou have to bid the job based on the contract documents. My opinions were directed towards those writing the contract documents. If the design calls for a the bare minimum, I do not expect the installer to bear the cost of improving it. Again just my opinion