I've heard contradictory information on this question and I was hoping someone could shed some light.
Article 705.95(B) provides the opportunity to have a neutral that is smaller than the ungrounded conductors at the inverter output if the neutral doesn't normally carry current. The neutral in that case can be sized to the same size as the EGC. However, 250.122(B) states that when the ungrounded conductors are upsized due to voltage drop the EGC also has to be upsized per 250.122(B).
Does this mean that the neutral must be upsized to match the EGC in these cases?
Thanks for your assistance.
Article 705.95(B) provides the opportunity to have a neutral that is smaller than the ungrounded conductors at the inverter output if the neutral doesn't normally carry current. The neutral in that case can be sized to the same size as the EGC. However, 250.122(B) states that when the ungrounded conductors are upsized due to voltage drop the EGC also has to be upsized per 250.122(B).
Does this mean that the neutral must be upsized to match the EGC in these cases?