Not much.But it only states that the combined conductor must be the larger of the two tables for grounding electrode conductor or equipment grounding conductor. What am I not seeing
As long as you compare the neutral size to the table requirement for the EGC rather than the table requirement for the GEC even though they are both the same physical wire.