Re: Neutral sizing
There is a difference between table 250.66 and section 250.66. The table is full size, and the section allows smaller sizes for certain types of GE.
The size of the grounded conductor is the larger of table 250.66 or art 220 load calcs. The service grounded conductor should really be colored white and green, as it has two functions.