Where in the code does it address having only one neutral under a screw in the panel?

gus

As far as I know, nowhere. It is a listing issue, from the manufacturer about the neutral bus. If each hole is listed for 1-#6 to 1-#14, then 2 wires is not acceptable.
 

guschash

Senior Member
Location
Ohio
Thanks guys, I knew I read it some place but I couldn't find it. Appreciate the knowledge I get from here.

gus
 

LEO2854

Esteemed Member
Location
Ma
Where in the code does it address having only one neutral under a screw in the panel?

gus

Here it is..

408.41 Grounded Conductor Terminations. Each grounded
conductor shall terminate within the panelboard in an individual
terminal that is not also used for another conductor.


Oh!

I see you already got the answer....:lol:
 
Last edited:

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The UL standard has required that for many many years. It was put is as code rule because too many installers were no reading the label on the panel that says you can only use one wire per terminal.
 