neutrals and grounds at main disconnect .

Status
Not open for further replies.

Gaston

Member
" Celtic " , responded to " mshields " , with a picture of a correct path to earth of a ground fault , on a question regarding bonding at the load of a service . Perhaps some of you might remember . ( I tried to insert the picture but I was un able to do so ) . I found the picture self explanatory . But it still leaves me with the question of the neutrals and grounds at the main disconnect . As we all know , at the first mean of disconnect we must bond or ground the load beyond that piont . though the path in the picture , " Celtic " displayed , shows it being correct ; what happens when we are connecting them at the main disconnect when we have the main breaker at the panel.? :rolleyes:
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Gaston, what was the name of the thread?

Roger
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I believe this is the thread
http://forums.mikeholt.com/showthread.php?t=87053&page=2&highlight=grounding

Is this the picture

1100199786_2.jpg
 

celtic

Senior Member
Location
NJ
Gaston said:
what happens when we are connecting them at the main disconnect when we have the main breaker at the panel.? :rolleyes:
Assuming the N-G connection at the Main Disco Panel (MDP).,....
Assuming you don't make a N-G connection at the MCB..all is well.
Assuming you do make a N-G connection at the MCB - Parallel paths..NFG.

In the image Dennis posted, imagine for a moment that the "load" with the fault is just another panel, all paths back to the MDP can be subject to objectionable current.
 

haskindm

Senior Member
Location
Maryland
If you have a main disconnect ahead of the distribution panel the distribution panel is a sub-panel. The presence of a "main breaker" does not change this. Perhaps it should be called a "Master Breaker" in that it would disconnect all of the circuits in the sub-panel. The Main Disconnect would still be the Main Disconnect and that is where the neutral/ground connection would be. I hope I am understnding your question correctly.
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Gaston, I think of it this way: The service is usually the first point that the NEC has full control of an installation. They want the equipment grounding system (the system to provide an effective return path for a ground fault) to start as soon as possible, and then be seperate from the neutral current path.

Essentially, every point after the service disconnect should be bonded using the EGC, there shouldn't be a neutral connection to the exposed metal of an electrical system after that point. (There are a few exceptions to this general rule.)
 