(B) Multiple Circuits.
Where more than one neutral conductor
associated with different circuits is in an enclosure, grounded circuit conductors of each circuit shall be identified or grouped to correspond with the ungrounded circuit conductor(s) by wire markers, cable ties, or similar means in at least one location within the enclosure.
Exception No. 1:
The requirement for grouping or identifying shall not apply if the branch-circuit or feeder conductors enter from a cable or a raceway unique to the circuit that makes the grouping obvious.
Exception No. 2:
The requirement for grouping or identifying shall not apply where branch-circuit conductors pass through a box or conduit body without a loop as described in
314.16(B)(1) or without a splice or termination.