mbrooke
Batteries Included
- United States
- Technician
What code sections forbid the neutrals on ground bars in the main panel? Code book isn't in front of me. Also, would an isolated ground bar be ok as an add on neutral bar?
200.2 General. Grounded conductors shall comply with
200.2(A) and (B).
(A) Insulation. The grounded conductor, if insulated, shall
have insulation that is (1) suitable, other than color, for any
ungrounded conductor of the same circuit for systems of
1000 volts or less, or impedance grounded neutral systems
of over 1000 volts, or (2) rated not less than 600 volts for
solidly grounded neutral systems of over 1000 volts as described
in 250.184(A).
(B) Continuity. The continuity of a grounded conductor
shall not depend on a connection to a metallic enclosure,
raceway, or cable armor.
I do not believe there is any rule that prohibits that.
And no objectionable current has nothing to do with it.
I think he is probably well aware of the rule here just maybe misunderstood specifically what you were asking about, misread what you said or something like that.I don't get why Iwire is saying its ok... unless there is a jumper wire between the ground and neutral bar... but that still doesn't make sense.
This is what is not prohibited by code........I don't get why Iwire is saying its ok... unless there is a jumper wire between the ground and neutral bar... but that still doesn't make sense.
I could try to explain it but it is quicker to just admit I read your question wrong. :ashamed1:
That being the case I agree with the others.
The enclosure can be a part of path for equipment grounding conductor, it can not be part of the path for the grounded (neutral) conductor. So if the only continuity between a particular bar (in a service equipment or first disconnecting means of SDS enclosure) and the incoming grounded conductor involves using the enclosure you can only land equipment grounding conductors on that bar.Its ok. Ive read stuff wrong here more than once, more like every other thread :lol:
To be honest you got me thinking because I know you are a code expert. I actually thought you were right, and assumed that 200.2 (B) meant that the enclosure can not be the sole (depending entirely on it) conductor over to the neutral bar and assumed that a jumper would relieve that... but you have me in thought... could a large enough jumper allow for that loop hole?
....but the main grounded conductor bus in the service equipment can have both grounded conductors and equipment grounding conductors connected to it.
Can it? I think if you really look at the wording, this is not code complaint (although it is nearly universally accepted :angel![]()
(5) Load-Side Grounding Connections. A grounded conductor
shall not be connected to normally non?current carrying
metal parts of equipment, to equipment grounding
conductor(s), or be reconnected to ground on the load side
of the service disconnecting means except as otherwise permitted
in this article.
(4) Main Bonding Jumper as Wire or Busbar. Where the
main bonding jumper specified in 250.28 is a wire or busbar
and is installed from the grounded conductor terminal
bar or bus to the equipment grounding terminal bar or bus
in the service equipment, the grounding electrode conductor
shall be permitted to be connected to the equipment
grounding terminal, bar, or bus to which the main bonding
jumper is connected.
Which section do you claim disallows that?Can it? I think if you really look at the wording, this is not code complaint (although it is nearly universally accepted :angel![]()
I'm not aware of any code section that prohibits neutrals on the groundbar (or vice versa) at the location of the main bonding jumper. Most service panels I see don't even have a separate groundbar installed. If they do then there needs to be a jumper directly between the bars, but often that is factory installed.
If the GEC can land on the EGC bar why would you think an EGC couldn't land on the neutral bar? In the main service of course.
How do you see it as not code compliant?