What's the big deal. If you noticed most of the new Leviton decora switches, GFCI and AFCI have a similar selfgrounder.
Oh well , No selfgrounding for you!
hmy:
I'm old and have never seen one before either. Curious though, it doesn't appear to connect to the Ground Screw Terminal.
Could this be a device to hold the Mounting Screw in place; now done with a cheap piece of Plastic?
JimO
I'm old and have never seen one before either. Curious though, it doesn't appear to connect to the Ground Screw Terminal.
Could this be a device to hold the Mounting Screw in place; now done with a cheap piece of Plastic?
JimO
The green EGC screw is threaded into the metal of the Yoke. . . and, although you can't see it openly, the male cord cap equipment grounding tine contacts to the metal of the Yoke.
All auto ground clips "hold the Mounting Screw in place" and, in addition, are tested and evaluated as part of the effective ground-fault current path from the yoke to the clip to the yoke mounting screw to the box.
That was my only thought, not sure why it would even be considered for grounding, is there one for the top mounting screw?I'm old and have never seen one before either. Curious though, it doesn't appear to connect to the Ground Screw Terminal.
Could this be a device to hold the Mounting Screw in place; now done with a cheap piece of Plastic?
JimO
No, but I really only deal with industrial applications and the minor fixes I do around the house, 99% of my boxes are plastic so it would only serve as a screw retainerSo you never seen one of these. I think eagle used the wire or was that pass Seymor.
View attachment 19152
What's the big deal. If you noticed most of the new Leviton decora switches, GFCI and AFCI have a similar selfgrounder.
Hubble recepts that have USB in them also have self ground wire on the yoke. but if the wire has egc it has to be on the green screw for resi use.
![]()
my AHJ wanted egc tied to yoke even in metal boxes.Yes, you would have to use the EGC in the cable if you have a nonmetallic box. But if the box were metallic you would only have to connect the box to the EGC when using a self grounding receptacle.