NolaTigaBait said:
yeah , i was talking about #3 nm feeder....why would you have to use #2?

If you read 334.80, it states that nm can be used for 60C unless you are derating. The final ampacity must not be more than 60C
 
man, i forgot about that one....thanks....one of the last jobs that i did with my ole boss...we had a 200 main breaker panel in front of the house and we fed a 2nd panel in the back with a #2 feeder!!!!....of course he was going by 310.15b and I thought that this was ok, until i started reading on my own....the thing that doesn't make sense is that the main is fed with 2/0, but acccording to code, we would need a 1/0 feeder for a 125 main subpanel!!!
 
uhhhh, why i can't use let's say #4 for a 100 amp feeder where there are two panels in one house....why can't i use table 310.15b?....i understand why I can't use it....i want to understand the from the engineering aspect of it
 
NolaTigaBait said:
uhhhh, why i can't use let's say #4 for a 100 amp feeder where there are two panels in one house....why can't i use table 310.15b?....i understand why I can't use it....i want to understand the from the engineering aspect of it

Not sure, only that the NEC probably feels ART 220 is over rated for dwelling units.
 
NolaTigaBait said:
uhhhh, why i can't use let's say #4 for a 100 amp feeder where there are two panels in one house....why can't i use table 310.15b?....i understand why I can't use it....i want to understand the from the engineering aspect of it
It has to do with the diversity of the load. Table 310.15(B)(6) uses the diversity of the loads of a dwelling. When you split up the feeds that diversity is no longer applicable and you would need to use 310.16
 