Need to run a branch circuit in a mfg home, 30 Amp, 120 volt to a water heater. Circuit would run from panel, down to under chassis space , and over to bathroom.
I have never installed wiring in a mfg home, read thru Art 550, and would
1. Wiring under mfg home has to be protected and suitable for wet location, PVC with THHN/W
2. Branch circuit would have to be GFCI/AFCI protected
Branch circuit would cross where sections are joined. How is allowance made for future disconnection of sections?
Someone in the past ran romex for an outside condensing unit from the 200 amp service, thru the under chassis space (laying on ground) and out to condensing unit. Not sure what the inspector will say about that.