New house off the grid. Solar panels with battery backup. Someone else is taking care of that including the inverter. There will be 12V and 19V DC and 120V AC circuits. The 12V and 19V DC circuits are for computer/data equipment and maybe some lights. All wiring is being done in MC cable to reduce the EMF effect. (even the low voltage DC wiring)
1) I assume to meet NEC code I ignore the low voltage circuits and have 120V circuits that meet the 210.52 requirements of number, spacing, overcurrent and AFCI/GFCI protection? I understand there are requirements on separating low voltage wiring from 120/240V wiring.
2) Can you run MC cable to a light on an open porch if the MC is covered? (it is between the roof and ceiling of the porch)
3) Does a wall receptacle that is 30" above the floor meet the requirements of 210.52A?
4) Do the 12V and 19V circuits need overcurrent protection?
PS - would this off the grid house be required to be inspected in your state or locale?
1) I assume to meet NEC code I ignore the low voltage circuits and have 120V circuits that meet the 210.52 requirements of number, spacing, overcurrent and AFCI/GFCI protection? I understand there are requirements on separating low voltage wiring from 120/240V wiring.
2) Can you run MC cable to a light on an open porch if the MC is covered? (it is between the roof and ceiling of the porch)
3) Does a wall receptacle that is 30" above the floor meet the requirements of 210.52A?
4) Do the 12V and 19V circuits need overcurrent protection?