Just out of curiosity on residential work, with the need for AFCI's , does anybody megger the circuit before drywall just to be sure they are clear of faults or do you wait until a problem shows up? (tripping AFCI) Then trouble shoot the issue.
we dont meg I dont even know if we have a megger in the company. What I have done in the past when I know Its an area I will never be able to access again is Ill hook some temp power and make sure all boxes have power. We did this one time with a group of canlights on a church Knew we couldnt get back to them Really should meg but using my bosses mentality we just dont have the time theres always the next house to get to
It still might not find every problem, since you'll be manipulating the conductors when you put devices on, but it sure can't hurt.That is not going to show a nick in the insulation that may appear later on as a fault, I know this from experience. A Megger test takes no more time then what you did with a temp cord and is a lot more accurate.
For those who add circuits to mobile and modular homes, and rewire (in whole or in part) mobile and modular homes, the code requires you to megger the completed circuits.
Just out of curiosity on residential work, with the need for AFCI's , does anybody megger the circuit before drywall just to be sure they are clear of faults or do you wait until a problem shows up? (tripping AFCI) Then trouble shoot the issue.
110.7 Wiring Integrity.
Completed wiring installations shall be free from short circuits. Ground faults, or any connections to ground other than as required or permitted elsewhere in this Code.
now there's one I think I knew without any help from the NEC. Seems like common sense.110.7 Wiring Integrity.
Completed wiring installations shall be free from short circuits. Ground faults, or any connections to ground other than as required or permitted elsewhere in this Code.
now there's one I think I knew without any help from the NEC. Seems like common sense.
I dont have a count, but I have seen this in some trouble calls. It seemed as though instead of finding where the heutral had come loose the person would just tap off of the ground.now there's one I think I knew without any help from the NEC. Seems like common sense.
Seems like it , but how many times have you gone on a service call and found a ground/bond being used as a neutral ?
I dont have a count, but I have seen this in some trouble calls. It seemed as though instead of finding where the heutral had come loose the person would just tap off of the ground.
That can be deadly.
I remember a trouble call once where the tennants called the POCO first. I forget the original problem, but I went outside to check the sevice and found the ground clamp to be damaged and loose and went to start fixing it. I then got the crap knocked out of me. Come to find out the neutral connection had broke loose up at the pole and the service was trying to use the ground as the neutral.
That can happen without a 110.7 violation. A loose service neutral with a properly installed grounding electrode system will always do that - Ohms Law.I remember a trouble call once where the tennants called the POCO first. I forget the original problem, but I went outside to check the sevice and found the ground clamp to be damaged and loose and went to start fixing it. I then got the crap knocked out of me. Come to find out the neutral connection had broke loose up at the pole and the service was trying to use the ground as the neutral.
That can happen without a 110.7 violation. A loose service neutral with a properly installed grounding electrode system will always do that - Ohms Law.
The same can also happen if there is no isolation at the water metering - the metalic water line becomes a parallel path via the nieghbors house.That can happen without a 110.7 violation. A loose service neutral with a properly installed grounding electrode system will always do that - Ohms Law.