stickboy1375
Senior Member
- Location
- Litchfield, CT
I get it..... never mind...
Good cause I am ready for bed- laterstickboy1375 said:I get it..... never mind...
stickboy1375 said:The real question is this, is that UL sticker talking about 90* insulation, or 60* ampacity ?
334.112 Insulation
The insulated power conductors shall be one of the types listed in Table 310.13 that are suitable for branch circuit wiring or one that is identified for use in these cables. Conductor insulation shall be rated at 90?C (194?F).
334.80 Ampacity
The ampacity of Types NM, NMC, and NMS cable shall be determined in accordance with 310.15. The ampacity shall be in accordance with the 60?C (140?F) conductor temperature rating. The 90?C (194?F) rating shall be permitted to be used for ampacity derating purposes, provided the final derated ampacity does not exceed that for a 60?C (140?F) rated conductor. The ampacity of Types NM, NMC, and NMS cable installed in cable tray shall be determined in accordance with 392.11.
celtic said:60A wire for a resi fixture?
Bear in mind that the old rubber & bituminous compound insulations came, commonly, in three temp ranges.wireman3736 said:this house has mostly BX in the older part but it is surprisingly in very good shape and has a good ground according to my Ideal tester.
I feel comfortable assume that. If there is any doubt and it ain't marked you would be foolish not to assume the lower temp.al hildenbrand said:Bear in mind that the old rubber & bituminous compound insulations came, commonly, in three temp ranges.
R = 60?C
RH = 75?C
RHH = 90?C
One can't assume that BX is automatically a 60?C wire.
al hildenbrand said:Dennis,
I understand that "comfortable"-ness, but, Wireman notes that the BX wiring is in very good condition.
If he is finding good condition BX conductors in a j-box above a luminaire that is, say, the heat concentrating fishbowl enclosed incandescant that has been there for a long time, then I would feel comfortable in assuming that the insulation is higher temperature RH or RHH.
And when he cannot, what do you condsider the proper fix?Pierre C Belarge said:As an inspector, when I see a new fixture that requires the building wiring to be 90C, and there is BX installed, it is the contractors burden to prove to me the wiring is of the 90C type...
of topic a bit but ---romex that we use today -- we cannot prove what insulation is in there. We know it's 90 degree but we have no idea if it is THHN or THWN. I wish they would write it on the wireal hildenbrand said:Pierre,
As I recall, the only label required on BX was a single 2" x 4" paper tag wire tied to the 250' coil. Once that coil is broken and installed in lengths cut to fit, even the original installing electrician couldn't prove that a given piece of BX was from one coil or another.
I would go to that ceiling hugging incandescant fishbowl luminaire in the kitchen or hallway and see if the conductor insulation in the j-box was still flexible.