Anything 480 over 800 amps. limited to 70' But with permission I have done install like this to 150' but when you walked over the slab it sucked the nails out of your shoes. and it screwed up the screens on the PC in the office.
. . . the violation I see after you guys brought it up was 300.12. . .
Actually, that is not a violation. See Exception No. 2: Raceways and cables installed into the bottom of open bottom equipment, such as switchboards, motor control centers, and floor or pad-mounted transformers, shall not be required to be mechanically secured to the equipment. :)
We are using 05 and the only exception is for raceways for cable (sleeve) But enough of this. I thank every one for your input.