New parking lot LED mogul base screw in lamp for 1000watt 240 volt lamp
New LED mogul base lamps say rated for 120 volt through 277 volt. That means direct wire 240 volt and were good, but I thought code says that a screw shell of a lamp holder must always be grounded......?
It does, so that makes the usual sources of 208 and 240 rather problematic. But 277 should be OK from 480Y/277.
410.50 says that when "the grounded conductor, where connected to a screw shell lamp holder...". 2 ungrounded conductors can be hooked up either way. 208V, 240V and 480V lighting are perfectly legal. Corner grounded deltas would have to have C (grounded) phase to the shell and polarity would matter if using AC or BC legs.
Iow, if you're using a grounded conductor, it has to go to the shell but there is nothing saying you have to use a grounded conductor - 2 hots is fine.