You missed 240v.... We have 480v 277v 208v 120v panels. ...
You missed 240v.... We have 480v 277v 208v 120v panels. ...
You missed 240v.![]()
Have at it....... Since the OP seems like a good sport, shall we tell him how to determine this with a volt meter?
You missed 240v.![]()
Yep.
It would be interesting to see what the 240 panel really is though and why it is there. And does it come that way from the service. Could be 240Y/139, 240/120 delta center tapped or far more unlikely 240 delta ungrounded or 240 delta corner grounded. Since the OP seems like a good sport, shall we tell him how to determine this with a volt meter?
Well it looks like a separately derived system. I wonder if it is properly bonded to ground. A check of voltage from each phase to ground would be telling.
Any conductors connected to A phase in that panel are required to be identified as grounded conductors....white or gray.This is the feeder panel and transformer, have not opened but this is what I will shut off tomorrow to work in the 240V panel, so I could.
Any conductors connected to A phase in that panel are required to be identified as grounded conductors....white or gray.
Any conductors connected to A phase in that panel are required to be identified as grounded conductors....white or gray.
But we do see some.I was able to remove the face panel and sneak a peek inside, snapped a few pictures and this is one:
I don't see much white or gray at all...?
But we do see some.
That's better than none. :happyyes:
The disconnect says that A phase is grounded. This is a corner grounded system. The conductor connected to A phase is a grounded conductor and the rules in Article 200 apply.Well this is new to me. Can you or anyone else explain further? :?
Check voltages per Don's post.Although the ones that are there go into the other panel, looks like they are a type of gfi breaker with a neutral connection?
I believe the breakers in the panel are labeled "shunt trip" also
This is the feeder panel and transformer, have not opened but this is what I will shut off tomorrow to work in the 240V panel, so I could.
The disconnect says that A phase is grounded. This is a corner grounded system. The conductor connected to A phase is a grounded conductor and the rules in Article 200 apply.
To be sure that you really have a grounded system, you need to check the voltages. If A phase is grounded you will have the following voltages.
A to Ground = 0
B to Ground = 240
C to Ground = 240
A to B = 240
B to C = 240
A to C = 240
Was just able to finally check, checked off of a 3 pole breaker: top lug=245 middle lug=0 bottom lug=247
It appears corner grounded (assuming the values posted are line to ground) and using a 3Ø bus panel... but that doesn't tell you which phase is grounded. The middle lug of a 3P breaker can be positioned in the panel to connect to any one of the three busses.Was just able to finally check, checked off of a 3 pole breaker: top lug=245 middle lug=0 bottom lug=247