220.88 New Restaurants.
220.88 New Restaurants.
Guy, when you use a rule, you use it as written, includint tables and notes to table. The note to Table 220.88 is as follows: "Note: Add all electrical loads, including both heating and cooling loads, to calculate the total connected load. Select the one demand factor that applies from the table, then multiply the total connected load by this single demand factor." So when you are using Section 220.88 and apply Table 220.88, we then apply note to Table 220.88. Yes, we do include a/c and heat. It doesn't have to make sense, we just have to follow the specific rule. Section 220.61 is contained in Part III of Article 220, it does not apply to any rule contained in Part IV.