I think you are arguing just for the sake of arguing. I'm sticking to the OP's case, not some "what if" case. He has a branch circuit as he described.Apparently I am, and the consequences of certain interpretations to those other cases.
Which is silent on whether there are any controls in house for garage loads on that branch circuit. I'm not saying it's likely, it's just not ruled out by the OP, so the comment is directly relevant to the OP.
It's certainly part of a branch circuit, just probably not the entire branch circuit. It would still fall under 225.30, which is why 225.30(E) mentions it.
Cheers, Wayne
That doesn't help us, because the entire difference of opinion hinges on the breadth of the word "supply" in the title or first sentence of 225.30. Charlie's Rule doesn't tell us definitions. "Supply" is not an Article 100 term.Wayne, go back to Charlies rule
Entirely possible. : - )I think you are arguing just for the sake of arguing.
But you just made up the "at the building" part. It's not in the text.
Perhaps, but I think that's already covered by the other allowances in 225.30 and 230.2, such as parallel power production or different characteristics/uses. So that's not the meaning.I did come up with another meaning for "on the load side of a service disconnecting means." So that limitation has the effect that you can have two different non-grid based supplies to a building if there are no grid-based supplies to the building.
Cheers, Wayne
Doesn't "served by" already mean that the conductors have one end (sufficiently) far from the building, and the conductors power loads located in or on the building? I'm thinking they are just being redundant to emphasize something.It's implied by the whole thing. 'Building or structure ... served by a feeder or branch circuit on the load side of the service disconnecting means". If the service disconect is at the building then the building isn't served 'on the load side...'.
OK, let's say your PI has been accepted. I don't see how that changes anything discussed in this thread. Maybe I'm missing your point.I think if I put in a PI to change it to 'building or structure served by a feeder or branch circuit whose source of supply is through service equipment located at another building or structure', they would either accept it or else reject it on the basis that it already says that.
If the above is your point, and that the above would prohibit the arrangement in the OP, then:The meaning is: Where a feeder or branch circuit supplies a building from service equipment that is not at the building, then no other feeders or branch circuits shall supply the building whether or not their service disconnect is at the building. (That is, unless the other specific allowances apply.)
Good question. Also does 'served by' mean something different from 'supply'/'supplied by? If so, why once again, did they switch from 'served by' to 'supply' in the first sentence of 225.30? If 'served by' means what you suggest, but 'supplied' could mean any part or all of the conductors within the building or structure. In that case, for our OP, the existing branch circuit 'serves' the garage but the new branch circuits 'supply' it in violation.Doesn't "served by" already mean that the conductors have one end (sufficiently) far from the building, and the conductors power loads located in or on the building?
My point is simply that the the first sentence way 225.30 is written, the 'only one' circuit must be the feeder or branch circuit that 'serves' the building. Otherwise the building is 'supplied' by more than one feeder or branch circuit.I'm thinking they are just being redundant to emphasize something.
OK, let's say your PI has been accepted. I don't see how that changes anything discussed in this thread. Maybe I'm missing your point.
My reading so far has been that they mean the same thing. I'll ponder your points to see if I can divine an intended distinction. : - )Also does 'served by' mean something different from 'supply'/'supplied by?
Basically everything I've said about 225.30 applies to 230.2 as well:Also, I still say there's a 230.2 violation.
That yields a logical paradox--we can never supply a building with a branch circuit, because then it is also supplied by the feeder that supplies the branch circuit, and we've violated 225.30.To me supply means direct or indirect. A building supplied by a branch circuit is also supplied by the feeder which supplies the branch circuit and the service which supplies the feeder.
If you feel that is the intent, and there is or may be a loophole, why don't you submit a PI to change the first sentence of 225.30 toclearly the intent of both 225.30 and 230.2 is to generally prohibit multiple supplies of electricity being installed willy nilly to a building or structure without a good reason. . . . loophole . . .
I kept the original 3 way switch arrangement of 4 wires in conduit to a detached garage and ran a feeder to it for it's new use as a shop. Inspector didn't like it but when I pointed out that it had 1 interior light and one receptacle plus the switched outside lights and that was to provide emergency power to the building he gave me his that is a reach look but he handed me his signed green sticker.IMO the wording of 225 would prohibit the addition of a service.
225.30 Number of Supplies. A building or other structure
that is served by a branch circuit or feeder on the load side
of a service disconnecting means shall be supplied by only
one feeder or branch circuit.
Barring the specific allowances the words "Shall be supplied by only one feeder or branch circuit" means exactly that.
So if the building was already supplied by a branch circuit that is all that is allowed to supply it.
Dam I hope not. I used buildings to support a lot of stuff that had nothing to do with the building except that is were the load was mounted. Mostly that was for exterior lighting. If your use of "or on" is correct every outdoor light would have to be supplied from the building it is mounted on. One great example is wanting an exterior light so you can find your way to the garage safely. If I ran the 3 way switching circuit back from the garage end to make it possible to have control from the house were the service is located would someone see that as having 2 supplies to the house. I'm not saying that would be a legitimate application of 225.30 but this is getting very convoluted the way some people are looking at it.Doesn't "served by" already mean that the conductors have one end (sufficiently) far from the building, and the conductors power loads located in or on the building? I'm thinking they are just being redundant to emphasize something.