Service Grounding NEC 2020 Rhode Island
Underground service in 2 inch PVC Schedule 40
Conductors 4/0-4/0-2/0
Main breaker (Emergency / Service Disco) ATS Located at Pedestal Meter socket remote from house
MLO Panel located in homes basement
Ground rods located in Basement
Bonding jumper located in ATS and at Panel in basement
Argument: Since the ATS has the overcurrent protection.
-would the panel be considered a sub panel and a #6 ground be required to be pulled to provide a separate path for ground faults?
-would ground rods need to be relocated to the ATS
Remember RI is on the 2020NEC