So the GEC to water main and ground rod would have to both be bonded to the grounded conductor in the gutter
Sent from my SM-G950U using Tapatalk
There is one GEC from block to water pipe #6
Sent from my SM-G950U using Tapatalk
What size are the conductors from the meter to the first disconnect? These are also service conductors and there are 5 of them so if they are #2 then you need an even larger gec
No because note 2 would apply.If this installation were a meter center with main lugs and then bus bars to each socket/disconnect instead of "NEC conductors" in place of bus bars, would you size the GEC per the incoming 1/0 or to the ampacity of the bus bars?
Again read Notes 1 and 2What if it were 400 amp rated bus but only supplied with 1/0 conductor?
I still think the GEC needs sized per the incoming 1/0 conductor, what is used between the common junction point, meter and disconnecting means doesn't magically increase the current carrying abilities of the 1/0 that is coming in from the utility and it is my belief that this is what the GEC is intended to be sized to, it has no need to be able to dissipate more energy than can enter via those incoming conductors.