The GEC only needs connected to the service disconnecting means, or some common point ahead of the service disconnecting means, per NEC. Only time a feeder would need to connect to the GEC is if it is a separately derived system or the supply to a separate building or structure, but that would be a new GES at the separate building or structure
I agree with you try telling that to these inspectors when u need a sign off to get paid

Sent from my SM-N920P using Tapatalk
 
I agree with you try telling that to these inspectors when u need a sign off to get paid

Sent from my SM-N920P using Tapatalk
When I mentioned a misunderstanding, it wasn't necessarily you or other installers that are the ones who misunderstand;)
 
When I mentioned a misunderstanding, it wasn't necessarily you or other installers that are the ones who misunderstand;)
I got ya but that's what they want now I don't understand it either they want all the neutrals bonded with the gec to my understanding it should only be bonded at the first point of disconnect as you mentioned or the main disconnect

Sent from my SM-N920P using Tapatalk
 
I got ya but that's what they want now I don't understand it either they want all the neutrals bonded with the gec to my understanding it should only be bonded at the first point of disconnect as you mentioned or the main disconnect

Sent from my SM-N920P using Tapatalk

to my understanding it should only be bonded at the first point of disconnect as you mentioned or the main disconnect

Sent from my SM-N920P using Tapatalk

How can that happen when the metering is load side of the service disconnect. The neutral(s) in the metering are bonded to the meter enclosure. Metering is one example of load side bonding of the sytem neutral when the metering is load side and adjacent to the service disconnect.
 
How can that happen when the metering is load side of the service disconnect. The neutral(s) in the metering are bonded to the meter enclosure. Metering is one example of load side bonding of the sytem neutral when the metering is load side and adjacent to the service disconnect.
Meter centers like pictured often have isolated neutral. If you do bond the neutral you do so in the "mains" section, which can be main lugs, fused disconnect, circuit breaker. Apparently OP's has main lugs. Once you go beyond six tenants in a situation like that you must put the service disconnect ahead of the meters or else you have too many service disconnecting means.

Individual sockets usually have the neutral permanently bonded to the cabinet.
 
Meter centers like pictured often have isolated neutral. If you do bond the neutral you do so in the "mains" section, which can be main lugs, fused disconnect, circuit breaker. Apparently OP's has main lugs. Once you go beyond six tenants in a situation like that you must put the service disconnect ahead of the meters or else you have too many service disconnecting means.

Individual sockets usually have the neutral permanently bonded to the cabinet.
Your right the section off to the right contains main lugs neutral is bonded there as well

Sent from my SM-N920P using Tapatalk
 
Meter centers like pictured often have isolated neutral. If you do bond the neutral you do so in the "mains" section, which can be main lugs, fused disconnect, circuit breaker. Apparently OP's has main lugs. Once you go beyond six tenants in a situation like that you must put the service disconnect ahead of the meters or else you have too many service disconnecting means.

Individual sockets usually have the neutral permanently bonded to the cabinet.

Individual sockets usually have the neutral permanently bonded to the cabinet.

And the meter to the left of the meter combo units is a individual meter enclosure,

and as far as the meter combo i have seen them both ways if the single socket alone or both the single socket and the meter combo its bonded load side of the main service disconnect.

250.142 Use of Grounded Circuit Conductor for Grounding Equipment.
(B) Load-Side Equipment. Exception No. 2: It shall be permissible to ground meter enclosures by connection to the grounded circuit conductor on the load side of the service disconnect where all of the following conditions apply:
(2) All meter enclosures are located immediately adjacent to the service disconnecting means.
 
This is a pretty good topic thanks for all the input in all your opinions do u guys see any NEC violations

Sent from my SM-N920P using Tapatalk
 
Your right the section off to the right contains main lugs neutral is bonded there as well

Sent from my SM-N920P using Tapatalk
Since you are on load side of service disconnect that neutral shouldn't be bonded - but apparently your AHJ don't see it that way with their common bonding bus rule.

For now you say most occupants don't have a panel in their occupancy, when they do get one are they supposed to bond the neutral in them and run a bond conductor back to that common bonding bus?? If so this would make all sorts of possible parallel neutral paths - which is one thing NEC intended to prevent with the general rule of not bonding the grounded conductor past the service disconnect.
 
Since you are on load side of service disconnect that neutral shouldn't be bonded - but apparently your AHJ don't see it that way with their common bonding bus rule.

For now you say most occupants don't have a panel in their occupancy, when they do get one are they supposed to bond the neutral in them and run a bond conductor back to that common bonding bus?? If so this would make all sorts of possible parallel neutral paths - which is one thing NEC intended to prevent with the general rule of not bonding the grounded conductor past the service disconnect.
When the panels finally get installed u do Jo bond the neutral at the sub panel they don't want that

Sent from my SM-N920P using Tapatalk
 
When the panels finally get installed u do Jo bond the neutral at the sub panel they don't want that

Sent from my SM-N920P using Tapatalk
Your meter center and panel in the area are the same thing - just with less feeder length between them:roll:

The single meter socket could fly with the exception mentioned earlier - but is supposed to be immediately adjacent to the service disconnecting means. Your case is pushing that description a little.
 
I agree and it used to be that way here u only bond the neutral at the main

Sent from my SM-N920P using Tapatalk
 
It's a plp public lighting panel or a landlord panel the Poco wants any plp when there's 3 or more meters to be of the bypass type so that meter has to be separated in order to be a bypass

Sent from my SM-N920P using Tapatalk
 
It's a plp public lighting panel or a landlord panel the Poco wants any plp when there's 3 or more meters to be of the bypass type so that meter has to be separated in order to be a bypass

Sent from my SM-N920P using Tapatalk

Similar thing here: did a job with 4 apartments and 4 commercial spaces. PoCo requires bypass for other than dwellings, so I had a stack of each.

Were the bypass stacks that much more that it was worth the wireway, conductor, etc over just buying one stack with all bypass?
 
Similar thing here: did a job with 4 apartments and 4 commercial spaces. PoCo requires bypass for other than dwellings, so I had a stack of each.

Were the bypass stacks that much more that it was worth the wireway, conductor, etc over just buying one stack with all bypass?

I was going to ask that.
 