Conductors shall be permitted to be connected to equipment rated according to Table 310.15(B)(6) when the installation complies with
all of the following conditions:
(a) The supply is a single phase, 120/240 Volt, 3 wire system.
(b) The conductors are installed for one-family, two-family, and multifamily dwellings.
(c) The conductors are either service laterals, service entrance conductors, or feeders.
(d) The conductors serve as the main power supply of an individual dwelling unit.
(e) If the conductors are a feeder, the feeder shall exist between the main disconnect and the panelboard that supplies 100% of the
load of the dwelling unit. This panelboard may supply that load either by branch circuits or by feeders, or both,
The feeder conductors to a dwelling unit shall not be required to have an allowable ampacity greater than their service entrance
conductors. The grounded conductor shall be permitted to be smaller than the ungrounded conductors, provided the requirements
of 215.2, 220.61, 230.42 are met.
4. Statement of Problem and Substantiation for Proposal: (Note: State the problem that would be resolved by your
recommendation; give the specific reason for your Proposal, including copies of tests, research papers, fire experience, etc. If more
than 200 words, it may be abstracted for publication.)
As the text currently stands, the first sentence of this section is very difficult to read, containing 56 words separated by no less than
nine commas. This section is packed with various requirements. It would be much clearer to understand, and more readily and
accurately applied in a list format. It is very easy to misapply this section as it currently stands. In addition: All circuits on the planet
have “either an equipment grounding conductor or no equipment grounding conductor”, so mentioning an EGC is just filler, unless the
panel is aware of a third option Iʼm missing. All chapter 3 wiring methods are either raceways or cables, so that language adds nothing
to this requirement either, and has been intentionally omitted. The term “main power feeder” hit the dumpster when grouped with
service conductors in list item (c) to reduce confusion. “All” was replaced by “100%” to strengthen the sentiment of the panel in the last
cycle. “...are part or associated with...” was not really necessary, in that the dwelling unit is what is diversifying our load - if a dwelling
unit serves an ancillary structure, it really has no bearing on the application of this section. Please accept this proposal at least in part,
as a list form will greatly clarify this section.