iustacould
Member
- Location
- Lexington, South Carolina
- Occupation
- Lead Electrical Contractor
Seems I have more questions than answers now days. I’m finding truth in the saying “The older I get the more I find out how little I know”
1000 amp 1 phase parallel UG service from POCO pad transformer to CT meter. Parallel 400 MCM copper from meter to Wire trough. Landed in power buss and split to multiple ATS and a few 200 amp disconnects all outdoor, then fed to interior panels throughout.
My confusion occurs with GEC size in 2017 NEC.
250.66(A) seems to apply seeing as I’m using rods as my electrodes with an IBT. Reading through other posts coupled with the overall size of the service worries me though. Wondering if I should actually apply table 250.66. I have to be over thinking this seeing as the exception is right in front of my face. Just wanted to see what the experts think. Big difference between #6 and 2/0.
All service equipment is outdoor. Single Family Dwelling with several outbuildings.
1000 amp 1 phase parallel UG service from POCO pad transformer to CT meter. Parallel 400 MCM copper from meter to Wire trough. Landed in power buss and split to multiple ATS and a few 200 amp disconnects all outdoor, then fed to interior panels throughout.
My confusion occurs with GEC size in 2017 NEC.
250.66(A) seems to apply seeing as I’m using rods as my electrodes with an IBT. Reading through other posts coupled with the overall size of the service worries me though. Wondering if I should actually apply table 250.66. I have to be over thinking this seeing as the exception is right in front of my face. Just wanted to see what the experts think. Big difference between #6 and 2/0.
All service equipment is outdoor. Single Family Dwelling with several outbuildings.