Doing engineering plans for the installation. The generator is a new 60KW generac 120/240v single phase with floating neutral. I understand that is a non-separetely derived system. Is t ground rod required. The automatic transfer switch is a2p- 400a with a 400a circuit breaker main. already installed in the house. The generator breaker will be a 2p-300a. IM a little confused about thye grounding
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The determination of SDS vs non SDS is based on whether the neutral is switched in the transfer switch.
If your TS is a two pole with solid neutral connections then the system is not and SDS and the generator neutral will be floating and have a EGC from the system to the generator.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Many are confused about generator grounding and bonding. Mike Holt once was working with generac about ground rods at generators, he gave up on that.
 