Lakeshore I never cared for them. Besides a PIA to get parts for I once blew a hole in my arm working on a Lakeshore. MY FAULT by Like Barbara says Memories
ASCO once the best still, decent.
Zeinth Decent
Russell Electric the bank vaults of ATS's.
When asked ASCO will provide a very decent "self-certified" SCCR for use with many different breakers. We have had little problem finding an ASCO switch (although not the inexpensive ones) that was not rated with whatever breaker was required for selective coordination.
So far, 12 months and at least 3 jobs, I have never gotten anything except the published SCCR data from Russellectric. Still have not found a combination of any of their switch and breaker for selective coordination that meets fault levels above 22kA.
Remember selective coordination is a requirement for required "backup" systems, it is not just for hospitals.