That's the most important issue in my opinion. I'm in the camp of "use it until you lose it" with regard to applying VFDs to older motors, but with respectful deference to that issue.... Now if downtime because of a failed motor is not worth it, you should definitely put on the correct motor, some instances that down time costs more then equipment repairs do.
I did a project at a glass plant to optimize the furnace blowers using VFDs. They were 1,000HP 460V motors and my competitor told them they did not need to replace the motors when adding the drives, they would "probably" last for years. I simply asked a series of relevant questions.
"What is the consequence of losing one of those motors, and how long will it take to get it repaired?". They responded that the furnace had two blowers so the 2nd one would allow them to continue operation, just at reduced capacity. But it also turned out there was NOBODY left in northern California capable of handling that big of a motor, it would need to be sent to So Cal, so it would likely be a week minimum turnaround even on a rush basis.
Question 2: "Do you have a spare motor?". No, we used to, but when we added that 2nd blower we used that motor because the lead time was too long, then the replacement spare has been left out of the budget for the last 5 years."
Question 3: "So if that one motor goes down, you have the other blower still working to keep the glass from solidifying, but with lost production capacity and no further redundancy if that SECOND motor goes down in less than a week from the first one then?". They thought about it and said yes, that was correct.
Final question: "What is the cost of lost production and having to get the solidified glass out of the furnace if that second blower fails while waiting for the repair on the first?"
Approximately $700,000 per day in lost production revenue, likely $500,000 or more to clean out the furnace if it ever lost heat for more than a few hours.
I suggested they buy one new inverter duty motor so that if/when one of the others failed, they could swap it out quickly with the new one, then repair the failed ones to the same level, eventually cycling through the old designs and winding up with more reliability. I won. Even though I also convinced them to put in load reactors, motor #1 failed in 6 months, motor #2 failed 3 years later (the one that had been the spare, so it wasn't as old), I was the hero. So now all three are upgraded to "inverter duty". They have not had another motor failure since 2006.