brother
Senior Member
Got a new project when they bought a new water heater and they need us to reconnect the circuit. It appears the circuit is too small for this size water heater, (that is in a ceiling most inconvient spot). 3000 watt 120 volt wh. They had a number #12, 20 amp circuit. They claimed it was a the same as before. I told them it appears someone did it wrong from start, . Even without the 125% calculation added in, its still above 20 amps.
Question that was asked, can they just change out the heating elements to smaller wattage ones, and let it go. I believe since it is brand new, it will void the warranty, (they should have just ordered the right one). but it should work. Not sure if it would be a UL listing NEC code issue, since it was manufactured with the higher elements. Is there an NEC violation here?
Question that was asked, can they just change out the heating elements to smaller wattage ones, and let it go. I believe since it is brand new, it will void the warranty, (they should have just ordered the right one). but it should work. Not sure if it would be a UL listing NEC code issue, since it was manufactured with the higher elements. Is there an NEC violation here?