Especially, when you have the customer asking you to do it wrong !
I now remember, I read it on a fortune cookie.
Especially, when you have the customer asking you to do it wrong !
like the others said, 2000 watt technically would be too much per NEC.I'd change it to a 2000 watt and not give it a thought.
That also means there's no room to pull another hot #12 and use 240 volts.... No room to pull larger wire (barely got number #12 currently there) because of other circuits in the box and conduits ...
Do the Math: A 160-liter water heater with a 3kW heating element will run for 3 hours (almost exactly) on a cold start.
Certainly not for an above the ceiling one, like the one in the OP.Is that a common size combination? I’d expect anything that big to have a pair of 4.5 KWs.
In reality probably not very often. NEC still says you must consider them to be continuous load. 422.13.Are water heaters a continuous load? I can’t imagine one running for 3 hours straight.
That also depends on how cold the start is. Where I am municipal water is warmer just from sitting in the piping system vs what the water coming directly from the aquifer is. If on a private well you usually have colder incoming water as a general rule. Mine is around 55F once you have purged the lines of warmer water. Municipal water could easily be 10 degrees warmer when there is low demand on the system. Or at my last place the incoming water was a little shallow in depth near the street as they had taken some dirt off top back when they paved that street. In really cold winters the frost level got closer to that depth you could tell the incoming water was colder and it did burst the line one year.Do the Math: A 160-liter water heater with a 3kW heating element will run for 3 hours (almost exactly) on a cold start.
4.5 kw you would think would be what is commonly stocked in a 240 volt rating anyhow. Other ratings likely cost more simply because of volume sold on that particular model and also normally be a special order.Is that a common size combination? I’d expect anything that big to have a pair of 4.5 KWs.
That also means there's no room to pull another hot #12 and use 240 volts.
(re-identifying a white wire is a violation in conduit, and there's a nonzero chance some other circuit shares this white wire)
Thanks for the math lesson.(160 kilograms of water) x (4.2 kiloJoues / kg · Kelvin) = 672 kJ/K
3 kW = 3 kJ/second
(3 kJ/s) / (672 kJ/K) = 0.00446 K/s
ΔT = 40K (10°C to 50°C)
40K / (0.00446 K/s) = 8960 s.
IIRC one liter of water has a mass of 1 kilogram. Dissolved content I imagine can change this some.One would need to consider derating as well since its raceway with other conductors in it.
My first thought was cable not raceway.
Maybe run a new MC cable.
Thanks for the math lesson.
Now in English please.
I'll get out my conversion calculator.
How did you get 160 kilograms. With small of elements. Volume effects calculated time at zero flow.
That also means there's no room to pull another hot #12 and use 240 volts.
(re-identifying a white wire is a violation in conduit, and there's a nonzero chance some other circuit shares this white wire)
Step up/step down and spend more than what the WH costs just so you can use the existing conductors?Boost to 277V? All in all _arrrrgh_.
Jon
I personally have never had to do the calculation for the heating of water per kilogram etc.. Thanks for the math info. We let the plumbers decide how big of a water heater to install in a place. We just let them know what circuit size would be needed. Good info to know, I was curious how the past old engineers came up with the continuous load calculation for water heaters.One would need to consider derating as well since its raceway with other conductors in it.
My first thought was cable not raceway.
Maybe run a new MC cable.
Thanks for the math lesson.
Now in English please.
I'll get out my conversion calculator.
How did you get 160 kilograms. With small of elements. Volume effects calculated time at zero flow.
Step up/step down and spend more than what the WH costs just so you can use the existing conductors?
Some guys like to step over dollar bills so they can pick up nickels.
I think the watt rating is at 125 volts too so at 114 volts you are looking at about 21 amps.For fun we could consider VD and re run the numbers for a 20 amp breaker/ #12 thhn branch circuit. Let go with a 6 (5%)volt drop @120v, 2000w 120v rated element.
Now are we good with no derating?
I do know 3% on branch is recommended.
Just fun math for those in the field why thing work when the should not according to the book.