My feeble mind combined with the way I read 240.21(A)(2)and (A)(3) tell me that a transformer secondary conductor and a tap conductor can not be sized to the next larger OCP per 240.4(B). Am I correct ?
My feeble mind combined with the way I read 240.21(A)(2)and (A)(3) tell me that a transformer secondary conductor and a tap conductor can not be sized to the next larger OCP per 240.4(B). Am I correct ?
Overcurrent protection shall be provided in each ungrounded circuit conductor and shall be located at the point where the conductors receive their supply except as specified in 240.21(A) through (H). Conductors supplied under the provisions of 240.21(A) through (H) shall not supply another conductor except through an overcurrent protective device meeting the requirements of 240.4.
someone slipped a (B) in there (B)(2) & (B)(3)
both state "tha ampacity of the __ condcutor"
there is no mention of "next higher"..it says ampacity
240.21(C) Transformer Secondary Conductors. A set of conductors feeding a single load, or each set of conductors feeding separate loads, shall be permitted to be connected to a transformer secondary, without overcurrent protection at the secondary, as specified in 240.21(C)(1) through (C)(6). The provisions of 240.4(B) shall not be permitted for transformer secondary conductors.