I’m planning on running 3-#2 copper thhn/thwn and 1-# 8 cu thhn/thwn cu wires inside lfmc to a remote distribution panel.
According to 310.16 in the 60 def column 2 is good for 95 amps
240.6 only had a 90 and a 100 as standard sizes
Because of this and my load being very small I should be fine to fuse #2copper on a 100a circuit breaker ?
According to 310.16 in the 60 def column 2 is good for 95 amps
240.6 only had a 90 and a 100 as standard sizes
Because of this and my load being very small I should be fine to fuse #2copper on a 100a circuit breaker ?