310.12(B) would NOT allow the #4 to be on a 100A OCPD. The feeder to the detached garage does not supply the entire load associated with the dwelling310.12(B) would allow the #4 to be on a 100amp OCPD, although I agree the derating for the continuous load is going to effect the circuit sizing.