Shujinko
Senior Member
I have a hospital application where we are providing lighting occupancy sensors in the egress corridors. The normal light fixtures are controlled by these occupancy sensors, the emergency fixtures (on life safety branch circuits) are on all the time and not controlled by the occupancy sensors. The AHJ has cited that we must comply with NFPA 101 7.8.1.2.2 and that if occupancy sensors are installed in the corridors...upon initiation of the fire alarm system the lights must turn on in the corridor (if they are off).
I am used to using the Wattstopper ELCU-100 or ELCU-200 which turns normal and emergency lighting (controlled by the occ sensor) on at the same time in the event of a fire alarm. But this case is different because only the normal lights are controlled by the occupancy sensor not the emergency light (life safety branch). How would I interface only the normal lighting with the fire alarm system?
What product could be used? How would it be wired?
I am used to using the Wattstopper ELCU-100 or ELCU-200 which turns normal and emergency lighting (controlled by the occ sensor) on at the same time in the event of a fire alarm. But this case is different because only the normal lights are controlled by the occupancy sensor not the emergency light (life safety branch). How would I interface only the normal lighting with the fire alarm system?
What product could be used? How would it be wired?