NFPA 59A is the standard for installation of LNG plants. This question is related to 59A and not the NEC but maybe other codes have similar wording.
NFPA 59A has a table which defines electrical classifications around various equipment and is pretty straightforward. Area classifications and boundaries are consistent with NFPA 497.
Separately, NFPA 59A says:
Fired equipment and other sources of ignition shall be located at least 50ft (15m) from any impounding area or container drainage system.
An source of ignition is defined in NFPA 59A as:
Appliances or equipment that, because of their intended modes of use or operation, are capable of providing sufficient thermal energy to ignite flammable gas–air mixtures. [54, 2012]
So if I want to install a circuit breaker or contactor or other arc producing equipment 25' from an impounding area, the electrical classification guidance in NFPA 59A would allow a general purpose enclosure. But would this be considered an 'ignition source'? And therefore be prevented from being installed at that location? Do people have experience with other codes with similar requirements? Why not just make a 50' Div. 2 area requirement?
I always interpreted the 'ignition source' to be fired equipment and not electrical in this instance. But now I am not certain.
NFPA 59A has a table which defines electrical classifications around various equipment and is pretty straightforward. Area classifications and boundaries are consistent with NFPA 497.
Separately, NFPA 59A says:
Fired equipment and other sources of ignition shall be located at least 50ft (15m) from any impounding area or container drainage system.
An source of ignition is defined in NFPA 59A as:
Appliances or equipment that, because of their intended modes of use or operation, are capable of providing sufficient thermal energy to ignite flammable gas–air mixtures. [54, 2012]
So if I want to install a circuit breaker or contactor or other arc producing equipment 25' from an impounding area, the electrical classification guidance in NFPA 59A would allow a general purpose enclosure. But would this be considered an 'ignition source'? And therefore be prevented from being installed at that location? Do people have experience with other codes with similar requirements? Why not just make a 50' Div. 2 area requirement?
I always interpreted the 'ignition source' to be fired equipment and not electrical in this instance. But now I am not certain.