coulter said:
dnem said:
... . How well is the door/cover actually bolted on ? . Does it provide any barrier protection against the flash/explosion or does it increase projectile risk ? . What is the weakest link on the cover or the attachment of the cover ? . Are the cover holes large ? . How much do the bolt heads overlap the cover steel ?
All that stuff makes a difference when a blast occurs.
David
David (and Zog) -
How do you support this opinion?
I don't see anything in 1584 or 70E that takes this information into account for an arc flash calculation.
I was answering WdeanN who had posted in post #9 that they had already done an analysis but were debating their internal policy of treating "
exposed energized parts" differently from nonexposed. . The subject was no longer the arc flash calculation but rather determining the logic or illogic of their policy. . My conclusion was:
“All that stuff makes a difference when a blast occurs.”
My point being that if you decide to allow untrained people to reset breakers in your plant without any PPE, you are making an
arbitrary decision without considering either NFPA70E
or thinking thru the issue. . When talking about projectile risk or weakest link or bolt heads, I was talking about thinking thru a policy, not analyzing an arc flash calculation.
WDeanN said:
post #7
I would really like to see this cleared up. At our facility we require arc flash PPE to operate a fused disconnect with the door closed, but do not require PPE to operate 277V switch rated breakers with all covers on.
Generally we also require arc flash rated PPE if there are "exposed energized parts."
WDeanN said:
post #9
zog-
We are conducting an analysis. We are providing labels at all 480V and above panels, disconnects, switchgear, etc.
The question has come up about when to wear PPE? What tasks require it. We are trying to follow the same tasks as 70E, but generally provide caveat for "exposed energized parts."
You’ll see he said they had conducted the analysis and were now looking at how to apply it.
coulter said:
What you are advocating might be a good idea - might even be a great idea - just not supported by any peer reviewed literature or testing.
carl
And that was my point. . What happens
after the arc fault calculation is application of logic and the making of policy.
David