zog -
zog said:
Arc flash PPE requirements and boundaries apply when interacting with switchgear, no mention of exposed live parts. ...
I'm not finding this in 70E or 1584. If fact:
70E Article 100 - Definitions:
"Flash protection boundary. An approach limit at a distance from exposed live parts within which a person could receive a second degree burn if an electrical arc flash were to occur."
zog said:
...All arc flash analysis assume the door or panel will fly open. ...
I will need some help here. I couldn't find anything on this in 70E or 1584.
All of the models are for open air, or a three sided box. Now does that mean the bolted cover blew off or the work was being performed with the dead front off or open? I can't tell. 70E, Table 130.7.C.9.a certainly appears to lend belief that the covers will remain in place. For the equipment the OP is discussing, 480/277 lighting panelboards:
CB operation with covers on is Haz Cat 0
CB operation with covers off is Haz Cat 1
I did check UL 67 on panelboards and as you said, the hinged cover can open, but only up to 60 degrees. And as jim said, the shell can't be distorted such that live parts are exposed.
I got to wonder, if arc fault calcs assume that a bolted dead front is going to be blown off a panel, what use is the PPE when that missle is stuck in one's head?
I suspect I am missing something. Do you have any additional references I could read?
carl