bobby ocampo

Senior Member
Why is it not referred more often since Code says that Compliance therewith and PROPER MAINTENANCE will result in an installation that is essentially free from hazard....

Should the code emphasize PROPER maintenance in all the electrical equipment and refer to NFPA 70B?
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Don already expressed the primary difference. I will expand on that a bit. The NEC primarily focuses on installations that are intended to be visually inspected before some form of approval to energize. The fact that it doesn't always (or even usually) happen is irrelevant. Maintenance is rarely inspected by an enforcing authority after the initial permission to energize. Only subsequent failures warrant their attention, usually by State or Federal OSHA, a Fire Marshal, or Insurance Agency.

Second, NFPA 70B is only a "Recommended Practice" and, by NFPA general rules/regulations, is not intended to be adopted by AHJs, local or otherwise. See Part 2.4 of the NFPA Manual of Style.

BIG NOTE: OSHA agencies can and will enforce 70B after the fact under its General Duty Clause where failure to properly maintain is a "recognized hazard" by the industry involved.
 

bobby ocampo

Senior Member
If Maintenance greatly improves safety, Why not require periodic test and inspection of electrical wiring to be submitted to the AHJ? Test results may be required by AHJ if proposed in the Code or at least refer NFPA 70B to be the guide for PROPER maintenance.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
If Maintenance greatly improves safety, Why not require periodic test and inspection of electrical wiring to be submitted to the AHJ? Test results may be required by AHJ if proposed in the Code or at least refer NFPA 70B to be the guide for PROPER maintenance.

Periodic safety inspections of wiring are in fact done is some european countries, so it is not unworkable. But adding that additional structure and expense to our system would not be a simple transition. And, of course, somebody would have to produce a study showing that the safety benefits justify the additional cost to society.
 

luckylerado

Senior Member
If Maintenance greatly improves safety, Why not require periodic test and inspection of electrical wiring to be submitted to the AHJ? Test results may be required by AHJ if proposed in the Code or at least refer NFPA 70B to be the guide for PROPER maintenance.

AHJ's do not have the time for something like that nor are the funded for such an obligation. Proper maintenance is the responsibility of the owner and needs to be done IAW the manufactures instructions. I have not seen 70B but it is my educated guess that it is full of "according to manufactures instruction" language.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
If Maintenance greatly improves safety, Why not require periodic test and inspection of electrical wiring to be submitted to the AHJ? Test results may be required by AHJ if proposed in the Code or at least refer NFPA 70B to be the guide for PROPER maintenance.
It is important to recognize the National Electrical Code isn't enforced nationally. The closest is FedOSHA and its "Final Rule" is based on the 2002 NEC; it doesn't generally include residential occupancies either.

Local enforcement is up to State or various municipal adoptions. Even then, the latest edition is not necessarily adopted and several local adoptions include amendments that may even remove requirements.

One of the most common reasons for rejecting Public Input (Proposals or Comments) is, "How will this suggestion be enforced?".
 