Not strictly the NEC but ...
Section 13.2 Identification of Conductors
Two issues in particular have raised eyebrows in our facility.
13.2.4.1: Yellow for remotely energized conductors has been replaced by Orange that was used for High Leg.
13.2.4.3(1): Black must be used for all ac or dc power regardless of voltage. So tapping off my 120VAC single phase power supply can no longer be Red in a panel. And tapping off my 24VDC power supply can no longer be Blue in a panel.
Section 9 Control Circuits and Control Functions
Except of course 13.2.4.3(2) Red and 13.2.4.3(3) Blue when my power supply is used for controls only.
Section 13.2 Identification of Conductors
Two issues in particular have raised eyebrows in our facility.
13.2.4.1: Yellow for remotely energized conductors has been replaced by Orange that was used for High Leg.
13.2.4.3(1): Black must be used for all ac or dc power regardless of voltage. So tapping off my 120VAC single phase power supply can no longer be Red in a panel. And tapping off my 24VDC power supply can no longer be Blue in a panel.
Section 9 Control Circuits and Control Functions
Except of course 13.2.4.3(2) Red and 13.2.4.3(3) Blue when my power supply is used for controls only.