Duct Smoke Detectors
Duct Smoke Detectors
Placement of duct smoke detectors have been a troubling issue for many years now. NFPA and IBC, and previously BOCA, are in conflict on the location. One uses 2000 cfm, one uses 15000 cfm on return etc. Most designers in our area have ended up with a detector at 2000 cfm on either the supply or return air ducts, to satisfy both standards/codes.
The location is further compounded with the UL classification of the location relative to duct widths from inlets, bends etc. Typically, the UL location is not achievable due to the size of the duct and the length of run. Alternatively an air differential test is used to assure the detector and associated sampling tube actually works. Sampling tubes should extend the entire duct width as well.
Then there is the UL listing relative temperature extremes, most detectors are not listed below 32 degrees F, causing roof mounted duct work/detector locations very problematic. If the duct is planned well in design, the detector can be installed within conditioned space. Not caught, while in the field the issue is more problematic. Would love to hear folks methods to dealing with this particular issue, as many we have tried caused other problems. One was building a box around the detector, installing a resistant heating element, yet it caused condensation buildup in the box, resulting in other issues. Another was wrapping the detector with heat trace, yet there is issue concerning the UL listing of the detector with heat applied. Some have tried installing the detector in the AHU, yet did not address the concerns of if the AHU is turned off at night.
Duct detectors are not intended to sound the general fire alarm, their primary purpose is to shut the unit down, (unless you have an engineered smoke control system). Duct detectors report as a trouble signal. And, area detectors within the area the AHU serves is an alternate approach.
And, there is a cross trade issue, the installation of a detectors sampling tube , duct penetration, should be by a mechanic, under the auspices of the HVAC contractor. The detector should be provided under the auspices of the Fire Alarm Contractor/supplier. To connect the detector to a FA system, the detector should be UL listed as compatible with the FA system. Not all FA manufacturers will permit detectors of other manufacturers on their loops. Monitoring modules may be a solution to this issue, similar to the way we connect Sprinkler Flow and Tamper switches to the system.