Hi, Jraef,
Thanks for your reply. The common circuit I see is sourced from a 24VDC listed power supply. It is protected at its output for the rating of the supply. For our example let’s assume it’s 10amps. From this feeder OCPD it is ran to a terminal block strip. From this strip, multiple conductors are tapped off the terminal strip and land on their respective branch circuit OCPDs sized at 3amps. From here they land on additional terminal block strips to provide power for field devices. My understanding is that each conductor originating from the final terminal block to provide power for the device (i.e, limit switch, inductive proximity switch, photo eye, etc.) would be considered a tap conductor. From 7.2.8 we see that each tap condition must end in a single branch circuit OCPD. This is what lead me to interpret that each device must now have its own personal OCPD, which seems ludicrous and expensive to me.