assume a machine with 3 ph wye (or delta w/zig-zag derived neut) plus egc
a phase faults to the frame of the machine
a fault i returns to the X0
with no ngr only limitation is conductor and xfmr Z
frame rises to ph-n v (bad for guy touching machine)
all vdrop is across the egc, vn on the frame dropping to 0 at the X0
Now interpose an ngr in the ngr-X0 path
Fault current is limited by the ngr
so now the v drop is divided across the egc and ngr and fault i << less than no ngr
if vph is 480 then vn 277
total loop = ngr + egc = 18.5 + 2.5 (for example) = 21 Ohm
i fault = 277/21 = 13.2 A
across ngr 18.5 x 13.2 = 244
on frame 277 - 244 = 33 dropped along egc up to ngr(simple kvl loop)
Much smaller shock potential
all done for personnel protection
these faults are common in mining since cables (no conduit) is used
So this is in case the person comes in contact directly with a phase? Make sense, basically the NGR limits the current through the person.