Brian Baker
- Basye VA
If someone were to run two conduit pieces from a panel box to an LB or similar point and the conduit does not exceed 24 inches going into and out of the LB does this code reference still apply?
If you have a nipple 24" or less there is no derating required. Every pull point starts the 24" measurement over so if you had a 24" nipple into an LB and then into a 24" nipple, no derating would apply. If you had a coupling where the LB is then derating would apply.
Here a LB (or any condulet) is not considered a "similar enclosure" as boxes or cabinets and derating would apply to the installation you describe.
(4) Where conduit or tubing nipples having a maximum length not to exceed 600 mm (24 in.) are installed between boxes, cabinets, and similar enclosures, the nipples shall be permitted to be filled to 60 percent of their total cross-sectional area, and 310.15(B)(3)(a) adjustment factors need not apply to this condition.
310.15(B)(3)(a)(2) Adjustment factors shall not apply to conductors in
raceways having a length not exceeding 600 mm (24 in.).
310.15(B)(3)(a)(2) is the section applicable to my last post. If you have 24" raceways joined by a conduit body or a box the raceway has not exceeded 24".
So does this mean that one could theoretically build a 20 ft run, with C-bodies every 2 ft, and still take credit for the 24" no derate rule? Not that one would do that in practice, since I can't think of an example where it would be cost-effective, but it would still comply with the NEC.
Here 310.15(B)(3)(a)(2) is applied in conjunction with Note 4 to Table 1 of Chapter 9 which I included in my last post. The note to the table is interpreted here to say that a condulet is included as part of the raceway system as it is not a "similar enclosure" to a box or cabinet. The definition of "conduit body" seems to support this view. That is the way it is viewed here, YMMV.
Conduit Body. A separate portion of a conduit or tubing system that provides access through a removable cover(s) to the interior of the system at a junction of two or more sections of the system or at a terminal point of the system.
Boxes such as FS and FD or larger cast or sheet metal boxes are not classified as conduit bodies.
Raceway. An enclosed channel designed expressly for holding wires, cables, or busbars, with additional functions as permitted in this Code.
It's not immediately clear to me from the Article 100 definitions whether a conduit body is a raceway. Here are the 2017 definitions:
Cheers, Wayne
That would be true if you believe that Chapter 9 Table 1 Note 4 overrides 310.15(B)(3)(a)(2).I don't think that's the question. I think the question is whether a conduit body is a 'similar enclosure'as compared to a box or cabinet.
Otherwise, the only question is whether a conduit body is a raceway or not. If it is, then you include its length when measuring the raceway length. If it is not a raceway, then you measure raceway length between conduit bodies.
Cheers, Wayne