ryan_618
Senior Member
- Location
- Salt Lake City, Utah
I was recently asked to consult on a hotel type of project that was exisiting, but was wired under the 2005 NEC. My client was an electrical contractor who saw NM cable above the suspended ceiling, and became concerned about the legality of it.
This rooms in this hotel met the definition of "dwelling unit", and they were wired as such. The GFCI and AFCI rules were complied with, etc. My client was concerned about the fact that the common areas in the hotel (corridors, etc.) as well as some commercial areas in the hotel (gift shop, kitchen, banquet hall) had NM cable above the suspended ceiling.
My initial reaction was that this was a violation. The more I look at it, however, the more I think it complies. Take a look at the definition of "multifamily dwelling" and tell me if you agree with me. I think I will submit a proposal and try to clear it up in 2011, but for right now, I think it is legal, even above the ceiling of the kitchen and restaraunt.
This rooms in this hotel met the definition of "dwelling unit", and they were wired as such. The GFCI and AFCI rules were complied with, etc. My client was concerned about the fact that the common areas in the hotel (corridors, etc.) as well as some commercial areas in the hotel (gift shop, kitchen, banquet hall) had NM cable above the suspended ceiling.
My initial reaction was that this was a violation. The more I look at it, however, the more I think it complies. Take a look at the definition of "multifamily dwelling" and tell me if you agree with me. I think I will submit a proposal and try to clear it up in 2011, but for right now, I think it is legal, even above the ceiling of the kitchen and restaraunt.